3rd Party MSTP controllers are not able to be discovered.

Issue

3rd Party MSTP controllers are not able to be discovered.

Environment

StruxureWare Building Operation

Automation Server (AS)

Cause

MAC address of the Automation Server's MSTP Network was not configured properly.

Resolution

Under the AS / BACnet Interface / MSTP Network the MAC address had been configured differently to the default value of 0. Change the MSTP Network MAC address from 40 to 0 and 3rd party controllers will be discovered properly.