A schedule was created in the ENC and imported into the ENS, but it can not be edited in the ENS

Issue

A schedule was created in the ENC and imported into the ENS, but it can not be edited in the ENS

Environment

Niagara G3 all versions, ENS, ENC-520, ENC-410

Cause

The imported schedule becomes the slave of the original (master) schedule. Only the master schedule can be edited. The slave schedule can not be edited.

Resolution

If the schedule is to be edited in the ENS, then the schedule must first be created in the ENS and then imported into the ENC.