Issue

AMT is Displaying Link 200 and a partial point address.

Environment

I/NET site

Cause

Error Message AMT is Displaying Link 200 and a partial point address

Resolution

AMT can report a LINK 200 + a partial point address. When this occurs the system has defaulted to an error handling code to let the system programmer know that there is a hardware addressing conflict in a direct connect system.

To correct this; open active profile in the I/NET configuration editor and modify the link configuration editor.

The error generally occurs when the host hardware address is different then the actual hardware address.

For example: 7801 Tap is addressed "0" and the Host hardware address is something other than "0". When connecting to a Host/Link/Lan tap (either a 78010 that connect directly to the controller lan or an emulated 78010 on a controller), the hardware address is always 0 and cannot be any different.

Please read TAP and Repeater TCON 101 for a more detailed explanation on configuration parameters.