Issue

Access Events not being delivered to the database.

Environment

Continuum 1.9x

CX 9680

Cause

No access events reported to the database

Resolution

The workstation setup for primary access server had several processes that were running that appeared to be related to a virus on the workstation. This workstation was fully open to the internet and it is suspected that this is where the virus launched. After stopping several of the suspected executables through task manager the access events started coming in. Run antivirus.