Issue

Need to Edit StruxureWare Building Operation Reports

Environment

SmartStruxure

Report Server

Report Builder 3.0

Cause

Users wish to directly edit or create customized versions of existing reports

Resolution

  1. Open Microsoft Report Builder
  2. In the Menu, Select Options
  3. Change the database path to "http://localhost/reportserver_SQLEXPRESS' Where localhost is changed to the PC name or IP address and SQLEXPRESS is changed to the installed instance of SQL
  4. Click Ok
  5. You can now open existing files on the server and save new files directly to the Reports Server.
  6. You must Synchronize the StruxureWare Reports Interface for newly published reports to be available from the StruxureWare Interface.