Issue

Selecting the correct actuator for the VTRE valves.

Environment

VTRE

M9B

EM9

Cause

The data sheet for VTRE is currently listing the following suitable actuators:

M9B-24:  860-1010-000
M9B-230:  860-1020-000
EM9:  860-1110-000

Also, it states the following:

"NOTE! The VTRE valves require that the
 actuators be adjusted for 90° rotational travel."

However, the EM9 listed in the data sheet is 180° rotational.

Resolution

The correct actuators should be the following:

M9B-24:  860-1010-000
M9B-230:  860-1020-000
EM9:  860-1100-000