Alarm entry in Active Alarm View shows point's alias instead of name.

Issue

Alarm entry in Active Alarm Viewer shows point's alias instead of name.

Environment

CyberStation

Cause

Problem with enhanced alarm logging and enhanced alarm delivery.

Resolution

  1. Shut down ALL CyberStations
  2. From the Continuum Database Initialization in the Server tab de-select Enhanced Alarm Logging and Enhanced Alarm Delivery then update the database.
  3. After update database completes, put back the Enhanced Alarm Logging/Delivery and update the database once again.