Alarms in Menta not coming into Vista if the output is connected to additional logic.

Issue

Alarms in Menta not coming into Vista if the output is connected to additional logic.

Environment

Menta IV

Vista IV Workstation

Alarm Queue

Cause

Many times Alarms will be used to start backup systems in the event of equipment failure. This is commonly performed by attaching the output of an alarm to additional logic which will route needed information to the backup system.

Resolution

Add a DELB (binary delay) to the output of the alarm before connecting the additional logic. This will allow the alarm to show up in Vista Workstation.