Issue

After drag/drop/copying a b3 to many other b3s an InfinityProgram called FiringOrder is listed with the other InfinityPrograms within some of the b3s 

Environment

1.94 standalone, b3 VAV controllers

Cause

Appears something went wrong with the drag/drop/copy. Possibly tried to copy to too many controllers.

Resolution

ContinuumAnalyzer identified the problem in the InfinityProgram Object Integrity Test and the Clean fixed it up.
 