Analog Input Configuration Objects (AIC) Description

Issue

Some AIC objects are pre-configured for the most common thermistors used in the industry. However in Building Expert, i cannot see the description of the AIC object until it has been added.

Environment

SmartStruxure Lite Multi-Purpose Manage

Cause

Feature not available on the MPM

Resolution

The description of each of the AIC object is available below.

AIC1 to AIC10 = Empty (Manually configurable objects)

AIC11 = 10kOhm Type II Thermistor Celsius

AIC12 = 10kOhm Type II Thermistor Fahrenheit

AIC13 = 10kOhm Type III Thermistor Celsius

AIC14 = 10kOhm Type III Thermistor Fahrenheit

AIC15 = 1 KOhms Pt1000 Platinum RTD Sensor Celsius

AIC16 = 1 KOhms Pt1000 Platinum RTD Sensor Fahrenheit

AIC17 = 100 Ohms Pt100 Platinum RTD Sensor Celsius

AIC18 = 100 Ohms Pt100 Platinum RTD Sensor Fahrenheit

AIC19 = 1 KOhms Ni1000 Nickel RTD Sensor Celsius

AIC20 = 1 KOhms Ni1000 Nickel RTD Sensor Fahrenheit