Analog Pulse Command Object

Issue

Analog Pulse Command Object

Environment

I/A Series R2

Cause

A standard I/A Series Analog Output object will send a value periodically or when there is a change of value. However, the lighting control system requires a pulse command type. 

Resolution

There is a 'Fp1Shot' object in the programlib library which can functions as an Analog Pulse Command. This object is located in tridiumx > programlib > util. 

If you go to the properties of the 'Fp1Shot' object, you can set the minimum and maximum values that allowed to be set. You can also set the delay time which determines how long the value should hold before being released. 
If you
go to the properties of the 'Fp1Shot' object, you
can set the minimum and maximum value allowed to be set. You can also set
the delay time which determines how long the value should hold before being
released. 