Are Xenta Servers supported in StruxureWare Building Operations?

Issue

Are Xenta Servers supported in StruxureWare Building Operations?

Environment

StruxureWare Building Operations v.1.2

Xenta 701, Xenta 711, Xenta 721, Xenta 731, Xenta 511, Xenta 527, Xenta 555

Cause

Want to use Xenta Server as a controller in StruxureWare Building Operations.

Resolution

No there are no special support for Xenta servers. But you can add then as normal LonWorks devices. You can only read/write SNVTs from the Xenta server.

Normal Lon rules applies here, you can have a maximum of 64 nodes to a segment (we recommend to keep it under that). TAC Xenta Server I/O modules will not be seen in StruxureWare Building Operation, but they will count towards the 64 nodes on the segment. See Lessons Learned Article #7070 for more information on Lonworks units in StruxureWare Building Operation.
 