Issue

Average space temperature on TAC Xenta 120-devices

Environment

TAC Xenta 121-FC

TAC Xenta 121-HP

Cause

TAC Xenta 121 is able to averaging the actual space temperature from different sensors, like from two room units, or one room unit and one Lon-sensor.

It is also possible to averaging up to three different Lon-sensors.

Resolution

This will also effect if you have a Lon sensor, but write direct to the SNVT-input (nviSpaceTemp), the TAC Xenta 120 device will still calculate the average between the entered value and the bindings.