Issue

Can B-Link repeaters be used with StruxureWare Building Operation

Environment

StruxureWare Building Operation site

Cause

Need to add repeater(s) for StruxureWare Building Operation

Resolution

For StruxureWare Building Operation Release 1.xxx and higher

For communication using RS-485, the versions of B-Link repeaters shown below were tested and passed for StruxureWare use.
 
Models known to be supported:
BACnet MS/TP Repeaters
 Part Number Description
 
 B-LINK-AC BACnet MS/TP Repeater, 120/240VAC
 B-LINK-AC-OP BACnet MS/TP Repeater, 120/240VAC, open class no enclosure
 B-LINK-DC BACnet MS/TP Repeater, 24VDC
 B-LINK-DC-OP BACnet MS/TP Repeater, 24VDC, open class no enclosure
Fiber versions of the B-Link repeater have not been tested and therefore are not currently supported. We hope to add support in one of the early versions 1.1 or 1.2