BACnet output point under the BACnet Interface of Automation Server indicates out of service

Issue

Created a BACnet digital output under the BACnet Interface in the Automation Server but the Out of service property indicates 'True' and get the error 'Property value out of range' when attempting to set the out of service to false.

Product Line

EcoStruxure Building Operation

Environment

  • WorkStation
  • Automation Server - AS
  • BACnet Interface

Cause

BACnet output must be associated with an IO Bus output.

Resolution

See Associate AS BACnet Interface IO points with points on the IO bus in SmartStruxure 1.4 and above for instructions on setting the associated value.