Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 

BACnet output point under the BACnet Interface of Automation Server indicates out of service.

Issue

Created a BACnet digital output under the BACnet Interface in the Automation Server but the Out of service property indicates 'True' and get the error 'Property value out of range' when attempting to set the out of service to false.

Environment

WorkStation

Automation Server - AS

BACnet Interface

Cause

BACnet output must be associated with an IO Bus output.

Resolution

See http://buildingskb.schneider-electric.com/view.php?AID=14934 for instructions on setting the associated value.

Tags (1)
Labels (1)
Version history
Revision #:
1 of 1
Last update:
a week ago
Updated by: