BACnet router for MSTP network is broadcasting from an unknown device

Issue

SBO v1.4 will not learn MSTP devices on MSTP Network #1354 on Cimetrics BACnet IP Server

Environment

SmartStruxure v1.4 

Cause

BACnet in SBO v1.4 and 1.5 does not work with BACnet routers that do not have their own device object.

The BACnet Router for Network #1354 is a Cimetrics device which is hosting the MSTP network where 97 devices will not come into SBO.

The trace log (attached) has many entries like this:

2014-09-17 19:46:29.105 [1176806464] nsp.pin.BACnet Router for Network #1354 is broadcasting from unknown device -- ignored (BACnetMain)

2014-09-17 19:46:29.110 [1176806464] nsp.pin.BACnet Unable to add proxy for device Device_96 (ID=96), CStatus=0x80050019 (BACnetMain)

2014-09-17 19:46:29.110 [1176806464] nsp.pin.BACnet Router for Network #1354 is broadcasting from unknown device -- ignored (BACnetMain)

2014-09-17 19:46:29.115 [1176806464] nsp.pin.BACnet Unable to add proxy for device Device_97 (ID=97), CStatus=0x80050019 (BACnetMain)

Resolution

BACnet in SBO v1.4 and 1.5 does not work with BACnet routers that do not have their own device object. It is fixed in future release v1.6.

Not much can be done about for sites with 1.4 or 1.5 unless the 3rd party BACnet router (in this case the Cimetrics device) has a configuration option to assign it a Device Id.