Issue

How many BBMDs and Foreign Devices can be registered on a CyberStation and a bCX4040?  

Environment

BACnet bCX4040 CyberStation BBMD Foreign Device 

Cause

Concerned about large BACnet sites and exceeding a limitation on the number of BBMDs and Foreign Devices that can be registered. 

Resolution

The maximum number of BBMDs that can be registered on a bCX4040 or on a CyberStation is 32.

The maximum number of Foreign Devices (FDs) that can be registered on a bCX4040 or on a CyberStation v1.93 or below is 64.

As of Continuum v1.94 CyberStation can handle up to 1024 FDs; the bCX4040 is still limited to 64 FDs.   