Issue

Double clicking the BACnetNetwork used to open the BACnet Device Manager now it opens a BCP Device Manager that looks just like the BACnet Device Manager?  What is the BCP Device Manager?

Environment

I/A Series (Niagara) G3

Cause

Installing Distech software to support their devices will result in the BCP Device Manager being installed for the BACnetNetwork.

Resolution

This is not an issue, just be sure to select the correct Device Manager for the devices you plan to work with.