Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 

Bacnet MSTP Network ID-Comm2 cannot be duplicated

Issue

Bacnet MSTP Network ID-Comm2 cannot be duplicated

Environment

  • bCX Controller
  • B4 Controller

Cause

If the MSTP Network ID-Comm2 is duplicated, you'll experience issues when trying to find bacnet devices.

Resolution

Bacnet MSTP Network ID-Comm2 cannot be duplicated

When commissioning a Bacnet Controller either BCX or B4, caution must be taken to ensure that the MSTP Network ID-Comm2 is not duplicated. On jobs that have bacnet systems running on the same ethernet, make sure to avoid using an MSTP Network ID that is already in use independent of our system. The default MSTP Network ID Comm2 setting is 2765.

Tags (1)
Labels (1)
Version history
Revision #:
1 of 1
Last update:
2 weeks ago