Issue

Instructions on how to configure a Bosch Integration on Version 3

Environment

Accessxpert

Version 3

Win 8.1 and above

Hosted

Premise

Cause

Configuring a Bosch Integration on Version 3 to communicate to Accessxpert. There are certain settings that needs to be configured from both the Accessxpert side and Bosch so that the integration can be seamless and function as designed.

Resolution

One of the first things when doing this Integration is to have the Bosch Appliance ordered and installed on the Network where the Bosch Panel resides. The device comes pre-configured from Feenics and all that is needed is to make the necessary changes in Accessxpert using the following steps:

1. Verify that the connected instance does have the Bosch Services Enabled by going to the Hardware Provisioning and looking at the Bosch Services 

2. Cick on the Bosch Services

3. This entry would come up automatically as it was preconfigured into the Hosted Instance by Feenics

4. Click on the Panels label and add the Bosch Panel Type from the dropdown

5. Enter the necessary values on the various fields that correspond to the Bosch Panel, the Password must match what the Bosch Panel is using

6. Import the Configuration and then save and close

7. On the Bosh Panel verify that the Port is set for Port 7700, Automation Mode is set to 2 and the Firmware is 2.0 or greater

  1. If changes need to be made, you need to first connect to the Panel from RPS > make the changes > sync to the panel > disconnect from the panel
  2. Go into the appliance and stop / restart the Feenics Bosch Service within Windows Services

8. Make the necessary changes if needed then save and recycle power

9. Bring up the Hardware Tree and verify that the Panel is Online and communicating

10. All preconfigured Areas, Points and Outputs will show up in Green, indicating that everything is working properly.