Brought in BACnet devices with duplicate names but now getting alarm about the duplicates.

Issue

Getting alarm about BACnet devices with duplicate name.

Do not want to see the alarm

Environment

BACnet

Cause

In SBO, BACnet device name uniqueness enforcement has been removed but an alarm is sent anyways to alert of the problem.

Resolution

Disable the alarm if you do not wish to see it in the alarm view.

This can be achieved by right clicking on the alarm in the Alarm Pane and 'Disable Alarm'