CSC 5252 / 5352 - Controller does not switch off.

Issue

The controller does not follow the programmed on/off times.

Environment

CSC

5252

5352

Discrete

Compensators

Cause

The flow temperature sensor has failed and is causing the controller to remain on.

Resolution

As part of it's "Out of Hours" operation, the controller will monitor the flow temperature and if it falls below 5'C, the controller will act to remove the risk of frost by starting the pump and opening the control valve.

For a full description of this function, please refer to the CSC User Guide.