Calendar entries from 3rd party BACnet devices viewable in WebStation

Issue

Calendar entries from 3rd party BACnet devices viewable in WebStation

Environment

StruxureWare 1.1.0.362

Cause

Are calendar entries from 3rd party BACnet devices viewable in WebStation? For calendar entries from third party devices that were not created through StruxureWare Building Operation, they are not shown in WebStation.

For example: When integrated a 3rd party BACnet device in StruxureWare Building Operation the integrator of this device created a calendar object on their side. Also created are so sample entries like 24th of December. When uploaded this device and viewing the calendar from the Workstation everything was fine but when viewing WebStation, the calendar entries that were created from the integrator are not shown.

Resolution

In Webstation 1.1 we only support Single date exceptions. We will support date range and calculated events in 1.2.
 