Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 

Can Continuum Engineering Units be changed and/or added to?

Issue

Can Continuum Engineering Units be changed and/or added to?

Environment

Continuum Cyberstation

Continuum Infinity Controllers

Continuum BACnet Controllers

Cause

Want to change or add an Engineering Unit as the unit I require is not present.

Resolution

Engineering Units are handled differently depending on the type of controller being used.

Infinity Controllers are able to have there units defined to be whatever you want (defined as up to 12 digits of text) in the Units field of the Input or Output object.

 

BACnet Controllers Input and Output Units are predefined by the BACnet specification and are chosen from a set list of Engineering Units. These cannot be changed or added to.


 