Can Xenta I/O modules be added directly to a Lon network?

Issue

Can Xenta I/O modules be added directly to a Lon network?

Environment

Xenta I/O modules

StruxureWare Building Operations Enterprise Server (ES) or Automation Server (AS)

Cause

The Building Operation ES/AS structure allows I/O modules to operate without an Xenta base unit.

Resolution

The following Xenta I/O modules can be added directly once the Lon interface and network has been created:

I/O Module DI DI status DO DO override UI TI AO AO override
Xenta 421A  - - 5 - 4* - - -
Xenta 422A - 4** 5 5 4* - - -
Xenta 451A - - - - 8* - 2 -
Xenta 452A - 8** - - 8* - 2 2
                 
* - DI, 0–10 V DC or 0–20 mA, 1.8/10 kohm TI        
** - Status indication only when the corresponding universal inputs (UI) are being used as digital
inputs.

For more details about how to configure Xenta Input and Output modules in StruxureWare Building Operation check this article LL#14268.