Issue

Can a Jace-Nxt installed with Niagara R2 be cleared and re-installed with Niagara G3?  It's from an existing jobsite that was R2 and is now being converted to G3.

Environment

Niagara R2

Niagara G3

Cause

Jobsite is upgrading from Niagara R2 and G3.

Resolution

Yes it is possible.  Use remote desktop to connect to the internal Windows desktop and proceed to install Niagara G3 as is done on any Windows box.

If the Jace-nxt has a hard drive, there will be plenty of free space to install Niagara G3.  If it has the flash drive, space is limited.  You may have to completely remove R2 to get the installation files for G3 copied over and installed. 

A G3 license will have to be purchased for the unit.

Note:  Tridium does not offer this 'upgrade' type of service.  It is a do-it-yourself task.