Can a Master schedule in a Niagara R2 Enterprise server station trigger slave schedules residing in a PollOnDemand object in a UNC station?

Issue

Can a Master schedule in a Niagara R2 Enterprise server station trigger slave schedules residing in a PollOnDemand object in a UNC station?

Environment

  • Niagara R2 Enterprise Server
  • UNC station

Cause

To trigger slave schedule, be sure to link a slave calendar to the slave schedule.

Resolution

Schedule objects do not care that the folder is PollOnDemand. Only driver points (ie. shadow objects) will be affected by the fact that their parent is a PollOnDemand container. Be sure that there is a slave calendar linked to the slave schedule in the same station. Calendar to schedule links do not work across an external link.