Issue

Existing site with a MSC-NC and several MicroSmart controllers no longer communicates.   The user cannot view real-time data.  The MSC-NC is proven defective.  Can a UNC-520 be used in place of the MSC-NC?  There are two, separate MicroSmart trunks connected to the MSC-NC.

Environment

DMS

Niagara R2

Cause

Product failure and obsolescence

Resolution

Remove the MSC-NC and replace it with the UNC-520 running a station with two MicroSmart Services - one per physical controller trunk.