Can an Infinity Controller with a Modbus xdriver operate as a slave node to a third party Modbus device that is set up as the master node?

Issue

Can an Infinity Controller with a Modbus xdriver operate as a slave node to a third party Modbus device that is set up as the master node?

Environment

Modbus RTU

Modbus TCP/IP

xdriver

Cause

Third party modbus Master has to poll data from a CX or BCX controller that is set up as a slave node.

Resolution

The Modbus TCP/IP xdriver can be configured to operate as a slave node.

The Modbus RTU xdriver must be the Master node whatever MODbus network it is attached to.