Can an analog value be totalized in a MNL controller?

Issue

On a jobsite, an energy meter was converted from a pulse output to a voltage output.  Can the analog input be totalized in the associated MNL controller like the pulse input was previously?

Environment

MNL

Cause

Changes on-site

Resolution

Analog values cannot be totalized in the MNL controller.  The next best option is to send the real-time analog value to the area controller (i.e. Niagara UNC or ENC) via a nvo and use the features available at that level for totalization.