Issue

Can not download application to a Xenta 401. The download looks fine until the file transfer should start. Then it just hangs and nothing happens.

Environment

Xenta 401

Cause

The problem is that a file transfer is already started for something else (trend logs or alarms) and only one file transfer can run at a time for each LON network.

Resolution

  1. Restart the Vista Server
  2. If that doesn't help, restart the Xentas to stop the ongoing file transfers