Issue

If a wireless system with a BCX is setup on comm2 and a few wired controllers are needed, can the wired controllers be added to comm2?

Environment

BCX

Wireless

Continuum

Windows XP 

Windows Server 2003

Windows Server 2008

Cause

Wireless and wired communication cannot be used on the same comm port. A comm port that has wireless selected is a different protocol than infinet or bacnet mstp. The comm port can only speak one protocol at a time.

Resolution

To use a wireless and a wired solution at the same time, 2 comm ports are required by using one of the following configurations:

9680 (1 comm port for wireless and 1 for wired)

2 different controllers (2 BCXs with 1 having comm2 enabled for wired, the other BCX with Comm2 for wireless)