Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 

Can you replace a B-Link with an Infilink200?

Issue

Are the Infilink and B-Link interchangeable or can they be converted?

Environment

Infilink 200

B-Link

Cause

Both units are RS-485 repeaters; is there a difference?

Resolution

You cannot convert from a Infilink 200 to a B-Link. They are both RS-485 repeaters, but the circuitry is slightly different to handle the electrical requirements of the BACnet MS/TP and the Infinet. You must use the correct unit for the network type you have.

The Infinet network and the Infilink200 allow you to have any network topology (Star, Bus etc) where the MS/TP along with a B-Link can only be wired in a Bus topology in accordance with the BACnet standard. Neither product contains any firmware that can be changed.

Tags (1)
Labels (1)
Version history
Revision #:
1 of 1
Last update:
3 weeks ago
Updated by: