Cannot get a new B3-866-v controller to come online

Issue

Cannot get a new B3-866-v controller to come online

Environment

Continuum

BACNet

MSTP device

Cause

Using a 250 Ohm terminator on the MSTP bus

Resolution

Replace 250 Ohm terminator with the correct 120 Ohm terminator on each end of the bus

If the b3 will still not come online and other controllers are, disconnect the mstp bus and wait 10 seconds and reconnect.