Change from ABA to Wiegand readers on a ACX7xx

Issue

Changing readers from ABA to Wiegand and getting card not in database

Environment

Continuum

ACX7xx

ACX700

Cause

When you change card readers from ABA to Wiegand on a ACX7xx controller you need to make sure you also change the switch and jumper positions also

Resolution

You will need to remove the cover of the ACX7xx to reveal the dip switches and the resistor like jumpers that you will need to change, please see the attached document for how to make these changes . Link