Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 

Changing the NetController Model Type between 9900 and 9940

Issue

Changing the NetController Model Type between 9900 and 9940

Environment

  • NetController CX9900
  • NetController CX9940

Cause

Update NetController model number in Continuum database

Resolution

  1. Backup the database.
  2. Shut down Continuum as precautionary measure
  3. Open the SQL Enterprise Manager
  4. Open the SQL Query Analyzer
  5. Select the ContinuumDB
  6. To change from 9900 to 9940, type in update infinitycontroller set CntrlType = 44 where UiName = ‘Infinity1’ and execute
  7. To change from 9940 to 9900, type in update infinitycontroller set CntrlType = 42 where UiName = ‘Infinity1’ and execute
  8. Please note that you must change ‘Infinity1’ to match the Uiname of your controller
  9. Start Continuum up again and verify that the change was effective