Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 

Clean db for Enterprise Server

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance.

Issue

How does one get a clean database for the Enterprise Server?

Environment

StruxureWare Buildings Operation site with Enterprise Server ES.

Cause

Need for clean database either for testing or start from scratch. 

Resolution

1. Stop Enterprise Server using StruxureWare Software Administrator

 

2. Then go to the location of your database using Windows Explorer. For this example it is C:/ProgramData/Schneider Electric EcoStruxure/Building Operation 2.0/Enterprise Server/db

software-administrator.png

 

 

3. Delete the following folders if (some might not exist): Configuration, Historical, Persistent, System, UDT

db-explorer.png

 

4. Start Enterprise Server using StruxureWare Software Administrator, the system will create a new folders and files as needed.

 

 

Note: Restoring a different database over the current database does not require the clean database state. Using the backup and restore procedure allows you to switch databases.