Issue

  • Clicking on Time Schedule in Xenta Server, gives this security warning
    Java has discovered application components that could indicate a security concern.
    Name:  se.tac.applet.toe.TOEApplet
    Block potentially unsafe components from being run? (recommended)
  • After clicking "No" it works to browse different Time Schedules without any problem.
  • After logging out and in again you get the warning again

Environment

TAC Xenta 5xx/7xx/9xx

Java 1.6.-19 or later

Cause

This is not the recommended Java version for this Xenta server version.

Resolution

Change the mixed code settings in the Java control panel. For information on how to do this go to: http://www.java.com/en/download/help/error_mixedcode.xml

 

OR

  1. Uninstall Java 1.6.-20 (or later)
  2. Install Java 1.6.-17