Compilation error when binding to priority array in b3 Script program

Issue

Unable to compile a b3 Script program if there is a bind to the priority array of a commandable property.

How to command an object at a particular priority in b3 Script program.

Environment

b3

WorkStation

Automation Server

Cause

Because of historical reasons ( that are outside the scope of this article) in the evolution of the b3 firmware, binding to the priority array of an object within a Script program in the b3 is NOT supported.

Resolution

To command an object from a Script program in the b3 at a specific priority the WriteProperty command MUST be used.

 