Continuously repeated errors in Standard Output Window of R2 (Niagara) station, "Set timer for tag: (an integer) :400" and "Clear timer for tag: (same integer)"...

Issue

Continuously repeated errors in Standard Output Window of R2 (Niagara) station,  "Set timer for tag: (an integer) :400" and "Clear timer for tag: (same integer)" . The integer increments by one about every second until it reaches 128, then reverses the count, counting down by one into negative numbers.

Environment

I/A Series R2 UNC with the GCM driver

Network 8000 GCM

Cause

The cause of the problem was resolved with the gcm-2.304.530b.v1.jar.

Resolution

This is considered a nuisance error, and was corrected in the gcm-2.304.530b.v1.jar.

Tags (1)
Labels (1)
Version history
Revision #:
2 of 2
Last update:
‎2018-09-11 02:23 PM