Continuum 2.0 SP1 -- Select Default System Listviews not returning expected results.

Issue

After installing Continuum 2.0 SP1 problems are found with two of the System Default Listviewis.

  • Errors This Month returns no results.
  • Personnel_Expired Cards shows all cards not just expired cards.

Environment

  • Continuum 2.0 SP1
  • Cyberstation
  • ListViews
  • Filters

Cause

Misconfigured Listview qualifier or filter. 

Resolution

Errors This Month

The filter in the listview configuration is set to Root\OneMonthToNow.  It should be set to Root\MonthToNow.

Personnel_Expired Cards

The listview qualifier needs to be configured as shown below.