Issue

The StandAlone workstation is not getting alarms delivered to the active alarm view.

Environment

Continuum Cyberstation standalone.

CX Controller

Cause

Alarms are not being delivered to the workstation. When the point is edited, the point shows that it is in alarm.

Resolution

  1. Cyberstation was gracefully shut down.
  2. Start Continuum Database Initialization for StandAlone
  3. Enhanced Alarm Delivery was deselected.
  4. Database was initialized
  5. Continuum was restarted
  6. Points were set to an alarm value
  7. Alarms were delivered.