Issue

When trying to change the value of point or change the description of a point and save and refresh, Continuum gets Save Object Error with the message of "You have attributes that have not been applied. Do you want to apply them  now?"

Environment

Continuum LAN Workstation

Continuum SU Workstation

Cause

There is not enough disk space available on the SQL DB Server.

Resolution

Secure disk space by deleting old log data in ContinuumDB or delete unnecessary files from the SQL DB Server.