Controller locks up on configuration of the Modbus TCP-IP XDriver.

Issue

Controller locks up on configuration of the Modbus TCP-IP XDriver.

Environment

Continuum Controller

Cause

The Device Comm Status point was created as an InfinityString instead of InfinityNumeric

Resolution

Delete the incorrect Device Comm Status point and re-create it appropriately as an InfinityNumeric.