Controlling command priorities and point values with Continuum workstation programs or controller infinity programs.

Issue

How to control command priorities in 3rd party controllers

Environment

Continuum Cyberstation

Bacnet Controller (BCX, B4920, B3)

Bacnet command priority

InfinityProgram (Infinity Program)

Cause

How to control command priorities and point values with Continuum workstation programs or controller infinity programs.

Resolution

  • Default setting for a workstation program priority level is ManualOperator priority 8
  • Programs located in the workstation: default command priorities can be controlled through Bacnet Preferences
  • Controller InfinityPrograms will need to use the WriteProperty (pointname, value, priority level) to set a different priority other than priority 10
  • To relinquish a priority level use Relinquish(pointname, priority level)
  • Reload controller

 


WriteProperty (object_name, value, priority, index)

  • Parameter  Description 
  • object_name 
  • Object name, including a full pathname, followed by a property name.
  • The object identifier and property identifier are combined as one argument.
  •  value  
  • This actual value to which the property is set.
  • This is optional.  If it is not present, then the next argument, priority, must be present to perform a Relinquish command.  (See the example in Relinquish.)
  •  priority 
  • The priority  number, ranging from 1 (highest) to 16 (lowest).This is optional.  It applies only to a set                                     commandable property.
  •  For controllers:  If it is not present, priority 10, if applicable, is used.
  •  For CyberStation: The value, based on the priority in the BACnet Preferences dialog, is used.
  •  index 
  • This is optional.  It applies only to an array-type BACnet property.  The index is ignored whenever it is not applicable.

 

Infinity controller samples:

This line will write the value of 22 to priority 10
BACnetDevices\BNet_4444\B3_885\B3Num1 = 22

This line will write the value of 33 to priority level 4
WriteProperty(BACnetDevices\BNet_4444\B3_885\B3Num1, 33 , 4 )

This line will relinquish the value for priority level 4 setting the value back to NULL
Relinquish(BACnetDevices\BNet_4444\B3_885\B3Num1 , 4 )