Could an TAC Xenta 421-A device send out SNVT values with engineering values?

Issue

When TAC Xenta 421-A is used as stand alone LonWorks node, a value read from an 0-10 VDC or 4-20 mA is sent only as 0-100%, is it possible to send as engineering values?

Environment

TAC Xenta 421-A

Cause

Then the TAC Xenta 421-A is used as a stand alone LonWorks nodes, the values from an analog input is always sent as nvoAnalog1-4, in 0-100%.

Only exeption is then using thermistor inputs, when the measured temperature is sent out as nvoTemp1-4.

Resolution

TAC Xenta 421-A used as stand alone LonWorks node, the values from an analog input is always sent as nvoAnalog1-4, in 0-100%, unless the input is configured from 1.8 kOhm or 10 kOhm thermistors..