Creating object causes empty error window to come up.

Issue

Trying to create an Infinity Schedule under ACX5720, when saving the object an error window comes up.

The error window does not contain an error message, only the word ERROR and an OK button.

The error happens even if creating the object in offline edit mode.

No problem creating the object under a different controller.

Environment

CyberStation

Cause

Corruption in database.

Resolution

Dump the controller to an ASCII file then delete the controller.

Import the dump file into the Continuum network to re-create the controller.

Deleting and re-creating the controller clears up the corruption in the particular controller object in the SQL database.