Cyberstation Online Help for Workstation editor Time Tab contains incorrect information.

Issue

Cyberstation Online Help for Workstation editor Time Tab contains incorrect information.

Environment

Cyberstation online help

Cause

The highlighted text in the Workstation Time Tab online help is inaccurate.   

Note: When entering this number, use the opposite sign (negative or positive) from what you actually want the system to write. For example, if you are 300 minutes (5 hours) ahead of GMT, enter:

-300

For example, if you are -240 minutes (4 hours) behind GMT, enter:

240

Resolution

Under UTC Offset, the Note should read as follows:

Note: When entering this number, use an negative integer to specify time zones to the West (earlier than) Greenwich Mean time and a positive integer to specify time zones that are to the east of GMT.

For example, if you are 300 minutes (5 hours) ahead of GMT, enter:

-300

For example, if you are 240 minutes behind (later than) GMT, enter:

240 

Tags (1)
Labels (1)
No ratings