DMS MicroSmart, Global point passing (broadcast) not working.

Issue

DMS MicroSmart, Global point passing (broadcast) not working.

Environment

MSC-L1000

MSC- MPC-001

MSC-P-751, MSC-P-752, MSC-P-753, MSC-P-754

MSC-P-1501, MSC-P-1502, MSC-P-1503, MSC-P-1504

MSC-V-510, MSC-V-511, MSC-V-521, MSC-V-522

MSC-V-751, MSC-V-752, MSC-V-753, MSC-V-754

Cause

The number of TXD and RXD broadcast channels are limited per controller type.

Resolution

The Level 11. controllers' MicroSmart Global Data Broadcasting capabilities are as follows:
MSC-L1000: TXD and RXD on 1-122 channels

MSC- MPC: TXD and RXD on 1-122 channels

MSC-P-75x: TXD on 1-122 channels. RXD on 1-24 channels.

MSC-P-150x: TXD on 1-122 channels. RXD on 1-24 channels.

MSC-V-51x: TXD on 1-122 channels. RXD on 1-24 channels.

MSC-V-52x: TXD on 1-122 channels. RXD on 1-24 channels.

MSC-V-75x: TXD on 1-122 channels. RXD on 1-24 channels.

 