DST error Domain: LonWorks

Issue

When trying to commission a controller into a LonWorks network in SmartStruxure you get a DST error.

Environment

  • WorkStation
  • LonWorks Interface

Cause

The DST error occurs during the commissioning of the controller when the DST settings are attempted to be downloaded.

Resolution

TAC Xenta 280 and 300 series Controllers

If the DST error occurs when commissioning a Xenta 280 or 300 series controller then check the label on the side of the controller. If there is no /N/P after the model number then it is not a network presentation controller and can not be commissioned in SmartStruxure. For more information see Lessons Learned Article #4743.